Monitor malfunctions and electrical problems
Bill Horne
bhorne at banet.net
Fri May 5 12:06:34 EDT 2000
TWIMC,
I asked for a professional opinion on the shaking monitor thread
and followups. Herewith: the word from my favorite Master
Electrician. Ahem.
Bill Horne
-----Original Message-----
From: Thomas D. Horne
Sent: Friday, May 05, 2000 11:11 AM
To: Bill Horne
Subject: Re: FW: last on X for now
> Very few offices have three-phase power. This is only used to
operate heavy machinery with
> large motors. It would be uncommon in an office environment,
although sometimes HVAC or
> refrigeration equipment needs it. No light fixtures ever run
on three-phase power, at
> least not unless you are talking about things like stage
lighting.
>
[snip] In multistory buildings ALL power
is three phase: this allows for very large cost savings in
circuit
layout and installation. The power to the lighting circuits in
large
office buildings in the US is not only multiphase but very often
a
higher voltage than the receptacle circuits. The reason that is
true is
that the watts available to provide lighting is the product of
the
ampacity of the circuit times the voltage of the source. A 120
volt
circuit breakered at twenty amps can provide a theoretical
maximum of
2400 watts. The same circuit supplied from a 277 volt circuit
can
supply 5540 watts. One four wire, three phase, twenty amp,
circuit can
supply 16620 watts of power. This is why three phase power is
the rule
rather than the exception in large office buildings. The
construction
cost savings are too great for any competent electrical engineer
to pass
up. [snip]
> The most common cause of monitor shake is RF hash. I would
doubt very
> seriously that there is an serious electrical problem causing
it.
> Sometimes a ground loop can do it, especially on an unbalanced
network
> topology (coax Ethernet).
>
One relatively rare cause of monitor malfunction is high voltage
on the
neutral of a multi phase circuit. This can be brought on by
excessive
voltage drop in the neutral caused by harmonic currents
generated by
things like computer power supplies. Since the neutral, or
grounded
conductor, has no over current protection, these harmonic
currents can
raise the current flow to a level higher than the circuit can
carry
without excessive voltage drop. The excessive drop can raise
the
voltage on the neutral, at the outlet, to twenty or more volts.
Since
the voltage available to the monitor is the difference between
the phase
conductor and the neutral conductor voltage any excessive
voltage drop
on the neutral will lower the apparent voltage at the outlets
effected.
This can cause erratic monitor performance without noticeably
effecting
the computer's performance.
Tom
-